Can I install a 50 amp breaker for both the car charger and the dryer? When I use the dryer I am not use the car's plug. It was 30 amps.
-
2Related: Adding an extra 240v outlet to dryer connection with switch for charging car – isherwood Dec 08 '21 at 16:17
-
2Related: What's a simple solution to have 2 NEMA 14-30 receptacles and switch power between them? – isherwood Dec 08 '21 at 16:18
-
2Related: Adding new 240v 30 amp outlet by tapping into existing NEMA 10-30 outlet box – isherwood Dec 08 '21 at 16:19
-
2Related: Can I share a 240V outlet between two devices? – isherwood Dec 08 '21 at 16:19
-
2Presumably you're also going to be upgrading the wiring between the breaker and the outlets involved? – Vikki Dec 08 '21 at 21:18
-
You can never be completely guaranteed that the dryer and car won't be drawing at the same time. – Criggie Dec 08 '21 at 22:32
-
The question as posed asks for a yes/no answer. Consider expanding the scope to ask for analysis of the proposed solution and for alternative solutions. – Spencer Joplin Dec 09 '21 at 03:34
-
1Employ a professional to do things like this. Don't even think about doing it yourself. The fact that you have to ask this question tells me that you don't understand how electricity works, which means that there is a real chance that your house will burn down and your insurance won't pay for it. And for what it's worth, the answer is no. You cannot do this. – Dawood ibn Kareem Dec 10 '21 at 09:38
3 Answers
NO WAY! You probably have 10ga wire to the dryer which is generally good for 30 amps. And now you want to pull 50 amps on the wire/cable? ....with the possibility of someone after you sell the house, runs the dryer and EV charger at the same time, potentially pulling as much as 80 amps on a 30 amp cable!!!!! Run dedicated circuits with appropriately sized wire/cable gauges and appropriately sized breakers.
What you are proposing is a total hack job, not safe, not code legal. If your house burned down and they knew of your setup, you'd probably be denied a settlement.
DO IT RIGHT!
- 23,214
- 3
- 40
- 81
-
8Crap, when I re-read my answers sometimes I come across too strongly, I don't mean to be an AH. Still, having to manually, consciously manage an electrical circuit these days is really bad. People expect just to plug things in, have them work, and are safe. Otherwise we're getting back to the electrical system of that old TV show "Green Acres" , ....darn showing my age by the reference! BTW, thanks people for the up votes! – George Anderson Dec 08 '21 at 18:19
-
28Stopping someone from burning down their house is not the time to be tentative. – ScottyD0nt Dec 08 '21 at 19:52
-
14@GeorgeAnderson you only said "no way" once, and barely mentioned how likely a burned down house is with this "hack", one could make the case your answer wasn't worded strongly enough. – nexus_2006 Dec 08 '21 at 20:01
-
12Not too strong, George. We've had a number of posts recently where an OP stated they knew it was wrong and not to code but would do it anyway. Bottom line you called it like it is, a hack job. It could have been worse, you could have used the same word three times in a sentence... lol stay safe – JACK Dec 08 '21 at 20:12
-
7WOW! Thank all of you for the support of my answer! Didn't expect that. I always try to be a "nice guy" but sometimes I can get pretty emphatic. + to all of you! THANKS! – George Anderson Dec 08 '21 at 20:41
-
Is there an actual safety reason why the circuit would need to be dedicated, or is it just a code thing? One could easily imagine a circuit robust enough to safely charge the car and dry your clothes at the same time. – Vikki Dec 08 '21 at 21:17
-
1@Vikki Let's just say "code things" and "safety" are very closely intertwined. Frankly, the code (NEC) doesn't really care if your installation works or not, just that it's safe, won't shock people or burn structures down. It's up to the installer to make sure it works. Regarding a dedicated or combined circuit for a dryer and EV charger, think about it, the pigtail to the dryer is probably 10 ga, rated for 30 amps, then you connect it to a 50 or 80 amp circuit. If the dryer had a bad problem and a short, which can happen, you'd be frying/melting the cord before the breaker tripped. – George Anderson Dec 08 '21 at 21:55
-
@GeorgeAnderson: When I wrote "robust enough to safely...", I kinda included "upgraded wiring" under that. – Vikki Dec 08 '21 at 21:58
-
What I mentioned just above is this isn't theoretical or meaningless code requirements. It's real world stuff. In fact, just personally, I had a dishwasher on a dedicated circuit that started tripping it's breaker, a normal (not GFCI or AFCI) breaker. Bad stuff. I DK a lot about appliance repair, so called in a pro. He found the control board was fried so badly that the connectors (plug style) had melted onto the prongs of the connection. Meant a complete new wiring harness and control board, since it was about 15 years old, I just opted for replacing it. – George Anderson Dec 08 '21 at 22:01
-
1This is a perfect answer. OP is clearly clueless and not really interested in learning anything about electricity - they just want their power problem to disappear by whatever means is cheapest. That attitude is careless and dangerous and deserves exactly this type of answer. – J... Dec 09 '21 at 11:51
-
1@J... Thanks much for the comment. You're right. When I bought my current house there was a detached garage (almost a shed), that had cables wire-nutted out side a box, switches just taped to a stud (no box), and, get this, the garage door opener plug prongs were directly connected to the wires from the cables! No box, not even an outlet, just taped!!!!! No proper grounding. Needless to say, I ripped all that stuff out and re-wired. But you are right, there are a lot of hack jobs out there, but this was the worst I've seen. – George Anderson Dec 09 '21 at 22:21
-
@GeorgeAnderson I think we both had the same previous owner, lol. Switches taped to studs, wire nuts dangling from crawlspace floor joists, reverse wired outlets, and a bootleg feeder from the furnace that had been powering a pot-house ventilation system from the induction blower and which had been simply cut clean and left hanging out of the side of the furnace - live only when the furnace was running, but right there where you could get your mitts on it. Heck, he even had an office power bar bolted to the outside of the house and spliced with an extension cord into a box in the basement. – J... Dec 09 '21 at 22:51
-
@J... WOW, just WOW. some peeps just act like this is a 3rd world country. What you found is way worse than what I found. Jeeze! – George Anderson Dec 10 '21 at 07:49
-
@GeorgeAnderson I don't know...that garage plug taped to the wires is something special! – J... Dec 10 '21 at 13:44
Option 1: Commission the EVSE at 30A breaker (not 50A)
The amperage on your EVSE is just a setting, because EVSEs work like this.
The dryer receptacles are not made for frequent interchange. However, if your dryer has a 4-pin socket (not 3-pin), and you're willing to swap plugs every single time, then you have one option: When you are commissioning the EVSE, set the circuit breaker size to 30A. This will cause it to charge at a lower rate, but it will be safe and legal to share a 4-prong dryer outlet.
You will need to change the EVSE's plug to a 14-30 type, but cords of that type are readily available cheap.
Option 2: For certain panels, use a "Quadplex" breaker.
This has a 30A breaker and a 50A breaker both, in the space of a normal 240V breaker. The 30A circuit goes to the dryer. The 50A circuit goes to the EVSE.
That means you run a new 50A circuit to the EVSE with new wires to the correct socket (NEMA 14-50 or 6-50). You would need #6 NM or UF cable. If you don't want to pay for that, look for a socket which is labeled "CU-AL" and "75C" and run #6 aluminum cable. Aluminum is fine if you use the goop and set the screw torques correctly.
You must get a quadplex breaker that is compatible with your panel, usually, the same brand. That is not possible on all panels. If you ask a question about your panel compatibility, take photos of it and a clear photo of the panel labeling, we can advise you here.
- 300,628
- 26
- 286
- 734
-
With option 2, He's have to run new wire for the EVSE so he could just use a regular 50A breaker... right? – JACK Dec 08 '21 at 13:49
-
No, you can't put multiple outlets on circuits for these appliances:
NEC 625.40 requires an individual branch circuit for EVSE.
NEC 110.3 says equipment UL/CSA/ETL Listed Equipment must be installed per the installation instructions which for your dryer likely says it needs to have a separate 30A circuit (like shown here on Whirlpool page 4 and 6).
A 50 circuit would not provide adequate protection for a 30A appliance, an overload of 150% wouldn't trip a 50A breaker.
- 17,999
- 2
- 15
- 46
-
I agree with most of your posts here, but isn't over current protection for the installed wiring and not the device? The device should have it's own, built in, over-current protection, right? Or am I missing something? – George Anderson Dec 08 '21 at 13:22
-
I think, @GeorgeAnderson, the assumption is that the 30A appliance is installed with #10 wiring on a 30A breaker. Upping the breaker size leaves both the appliance and wiring unprotected. Unless, of course, one can be certain that the wiring is big enough to handle 50A. – FreeMan Dec 08 '21 at 16:45
-
1@GeorgeAnderson: Many devices that are designed to be used with dedicated circuits don't have any internal overcurrent protection, but rely upon the existence of upstream protection. A stove might be designed to be suitable for use on a 30A breaker, but have internal wiring that would survive any fault that wouldn't trip a 40A breaker, in which case it could be used with either size breaker as convenient, but if one had a stove on a 200A circuit, no matter how beefy the wire between the breaker and the stove, bad things could happen if the stove developed an internal short. – supercat Dec 08 '21 at 19:04
-
@supercat :Agreed, it's hard to know how much internal over-current protection is in a device vs. the circuit supplying it. But think about it, suppose a calrod burner on a range shorted out, but not drawing enough power to trip a 50 amp breaker, melted wires and potential fire would be the result. I just DK enough to comment intelligently, but I would hope that the range would have sufficient internal fusing to protect itself. Maybe I'm just being naive...I just don't know enough about this stuff to comment intelligently. Thanks for your comment. – George Anderson Dec 09 '21 at 02:18
-
3@GeorgeAnderson You are mistaken. In-device overcurrent protection is not standard for high-power devices that are required to be installed on dedicated circuits. UL listing requires hooking things up in accordance with manufacturer instructions - if a range says "30A circuit max", you may not put it on a 50A circuit. It has been designed (and tested) to fail safely on a 30A circuit, not a 50A circuit. – nobody Dec 09 '21 at 03:31
-
@nobody My comment clearly indicated I wasn't sure, so that's why it's a comment, not an answer. Thanks for your contribution. ....George. – George Anderson Dec 09 '21 at 04:04
-
@nobody: On the flip side, it's not uncommon for devices like ranges to have specifications that allow for installation with more than one size of breaker. The amount of wiring within a range is small enough that making all of the wiring safe for use with a 40A breaker may be preferable to requiring customers with an existing 40A range to change their breaker. – supercat Dec 09 '21 at 15:41