I would like to know if it's allowed to run 10/3 Romex in 3/4 inch PVC pipe for 15 ft. outside under the floor of an open porch to be wired to a 30A power outlet for a portable 6500 watt generator.
Asked
Active
Viewed 591 times
1 Answers
2
No. Nonmetallic sheathed cable is not allowed in wet locations. NEC considers outdoor conduit a wet location.
You'll have to use THWN conductors, or other conductors/cables rated for wet locations.
If you use THWN conductors, you'll be able to fit 7 conductors through 3/4" Schedule 80 PVC (Table C.9), or 9 conductors through 3/4" Schedule 40 PVC (Table C.10).
-
10/3 UF-B is $2 a foot at the orange borg... – ThreePhaseEel Mar 26 '15 at 11:50