I have a circular junction box on my deck (outside) where I can presumably attach an outlet, and it is connected to a switch. I have string lights I'd like to permanently connect to to this outlet (they plug in normally).

What is the best weather-proof solution so that I can keep the lights plugged in, but have the outlet protected from the elements, and use the switch to turn them on and off?

Justin
  • 195
  • 5
  • 3
    A standard in-use wet location outlet cover should do. They all have interior capacity for plugged cords nowdays. Odd that your box is round, though. Was it intended as a light? – isherwood Feb 12 '21 at 17:03
  • Yes it was... but I want the new "light" to be the string lights – Justin Feb 12 '21 at 17:13
  • 1
    My first inclination is to use a weathertight cover with a Cord Grip Bushing, but anything besides a receptacle and in-use cover would likely run into UL (CSA,ETL,MET) Listing issues for the light string. – NoSparksPlease Feb 12 '21 at 17:18
  • An outside outlet will need to be GFCI protected. – JACK Feb 12 '21 at 20:27
  • What is the difference between a weather resistant GFCI and a standard GFCI? It likely also includes a conformal coating over the internal circuitry to protect them from condensation. – HABO Feb 12 '21 at 22:14
  • @NoSparksPlease - "a weathertight cover with a Cord Grip Bushing", +1. UL; w/e: just can't sell it. Is there code that says you can't hardwire an exterior string light? Same as a pendant, no? Basically this question but weathertight and a cord bushing instead of a box-to-box. – Mazura Feb 12 '21 at 22:31
  • 1
    @Mazura, yes. The code says to follow manufacturers instructions... once you cut the cord cap off and hard-wire a set of string lights... goodbye UL Listing and goodbye code compliance. Not that it wouldn't work though; I would do it... – Jimmy Fix-it Feb 12 '21 at 23:51
  • Note that NEC 590.3(B) sets a 90-day limit on holiday lighting type products – ThreePhaseEel Feb 13 '21 at 00:26

2 Answers2

4

You need a weatherproof 4/O to single-gang plate with in-use cover:

enter image description here

Jimmy Fix-it
  • 35,726
  • 32
  • 57
1

The right way to do this: Add a blank cover on that box and use a close nipple to add another rectangular outlet box below it. Then in that rectanglar box, install a GFCI receptacle (unless this is fed from a GFCI circuit breaker already). Then you can get what's called an "in-use" weatherproof cover for the rectangular box. In-use covers have a gasketed flip-up cover that also provides a small flanged opening at the bottom for a cord to come out.

enter image description here

The reason for the rectangular box is because they don't make in-use WP covers for round boxes, because round outdoor boxes are not made to house receptacles.

JRaef
  • 14,944
  • 1
  • 18
  • 40