I'm getting ready to install a new, dedicated 240 V circuit for a 4 hp table saw that I just bought1. The saw hasn't actually arrived yet, so I'm working off information in the user manual I found on the product's website.
The wiring diagram in the manual shows a 6-20 plug (snippet below). The power requirements elsewhere in the same manual shows that a 30 A breaker is required (snippet also below).
But 210.21(B)(1) of NEC states
Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
Exception No. 1: A receptacle installed in accordance with 430.81(B).
Exception No. 2: A receptacle installed exclusively for the use of a cord-and-plug connected arc welder shall be permitted to have an ampere rating not less than the minimum branch-circuit conductor ampacity determined by 630.11(A) for arc welders.
430.81(B) states
Portable Motor of 1⁄3 Horsepower or Less. For a portable motor rated at 1⁄3 hp or less, the controller shall be permitted to be an attachment plug and receptacle or cord connector.
After several hours of extensive Googling, I've discovered a few things:
- 20 A < 30 A
- 4 hp > 1/3 hp
- Table saw ≠ arc welder
Question
How do I satisfy the power requirements for this machine and stay code compliant? The 30 A breaker (with 10 AWG wire) and 6-20 plug seem to violate code. Is there something I'm missing? Are there exceptions for situations like this?
From the user manual, page 6:
and page 17:
1 Actually, I'm getting ready to install a sub-panel for the whole workshop. This circuit will be in that sub-panel.