I'm adding a circuit to my garage for an EV charger. Yes, I have pulled a permit. I live in Massachusetts.

Here's my plan:

I'll be adding a new 60 amp GFCI breaker to the panel. Yes, there is space in the panel. The GFCI is required because the new circuit is in the garage (210.8.A). The nominal load of the charger is 50 amps so 60 amp is appropriate.

Said panel is in the basement, diagonally below the garage. I plan on running the wires exposed up the basement wall, then over along the ceiling to below the basement floor. I'll add a small hole (meeting (304.A.1)) into the floor of the garage. The wires will run on through the hole, up the wall of the garage, along the ceiling, then down a post in the center of the garage. Since the garage space would expose the wires to physical damage (300.4), I will need to protect the wires with conduit.

For this, I'll be using steel EMT which satisfies this requirement (358.E). (I wanted to use schedule 80 PVC but the big box stores are out of stock).

The charger I'm installing can draw as much as 50 amps and calls for a conductor compatible with 90C. In order to satisfy the 1.25x requirement for constant loads ( 215.2.A.1 ), the wire should be rated for 62.5 amps. I'll be using THHN AWG 6 copper which is rated to 65 amps and 90C (B.2(1)). Total wire distance is less than 35 ft.

Questions I don't have answers to:

  • My charger only uses the two hot lines plus a neutral. What gauge does the neutral need to be? Citing the code for an answer would be appreciated.

  • I will be direct wiring the charger. The hole for direct wiring is on the bottom of the charger while the wires will be coming from above. Is there an elegant way for the wires to do a 180 degree turn?

  • I've read that water can condense on the inside of the EMT conduit. This can be addressed by adding weeping holes along the conduit. Should I be worried about this / address this?

  • Are there requirements about the hole between the basement and garage besides size (304.A.1)?

products I'm using:

charger

GFCI breaker

wire

the post

enter image description here

Doug Deden
  • 670
  • 4
  • 12
holmeski
  • 195
  • 6
  • 5
    Quite sure the charger uses ground and not neutral. Do you need 50amp charger, do a lot of daily driving, or is it more of a want because it is big? Panel might have open space, but have you done a load calculation yet to see how much extra power/amps are available? Hard wiring the charger instead of a plug in, you usually do not need GFCI breaker. Can save some money there. – crip659 Feb 18 '24 at 15:59
  • Yeah, you are right about the ground – holmeski Feb 18 '24 at 16:07
  • You say "wires", and "THHN", but you also say "exposed" in the basement. You seem to know a lot about code so I doubt you're planning to run exposed THHN through your basement ceiling. Do you mean, or why don't you, some kind of cable (NM, SER, etc) from the breaker panel until you are adjacent to the garage, put junction box there and begin your conduit in that junction box? Assuming that is less work / cheaper than running conduit all the way to the panel. – jay613 Feb 18 '24 at 16:08
  • I know almost nothing about code. I'm posting here so people can double check my work – holmeski Feb 18 '24 at 16:09
  • 5
    For someone who knows nothing, your question is well informed. So let me put it differently -- you can't run THHN except in conduit. Given the size of the cable, it won't be any easier to run cable than conduit, I think you should just run conduit end to end. If there are a lot of turns you'll need a lot of pull points. For the last one, a 180, a junction box below the charger may be a good idea (instead of 2 90s) but I'd like to see the pole. A photo of the pole and the charger would help. There are ways. – jay613 Feb 18 '24 at 16:16
  • Thanks! I tried to do my research before coming here. I'm happy to do conduit end to end. The post is square and wooded, just shy of 6" to a side. – holmeski Feb 18 '24 at 16:42
  • 3
    What is the total wire distance? I do not recommend designing something that operates at 90C (194F). The reason the wire is so hot is resistance which also results in voltage drop. Wire is expensive but I always choose the next larger wire size to reduce temperature and voltage drop. The answer by @manassehkatz-moving-2-codidact is excellent and I would chose the subpanel route that he recommends. – John Hanley Feb 18 '24 at 17:16
  • total wire distance is 35' – holmeski Feb 18 '24 at 17:19
  • 3
    Required reading for EV charger installs – FreeMan Feb 18 '24 at 21:43
  • 1
  • You say there's space in the panel for the breaker, but is there room in your load calculation to draw an extra 60 amps? 2) Most electrical supply places will sell direct to consumers, not just electricians - check them for your Sch 80. Probably cheaper there. 3) EMT will serve as your ground, so what you spend on that will be offset by not having to buy a 3rd or 4th wire for grounding. 3) Your "charger" link is to a google search, please [edit] to link directly to the product so we don't have to guess and aren't all tracked by google.
  • – FreeMan Feb 18 '24 at 21:49
  • 1
    Ah! Thanks, @manassehkatz-Moving2Codidact, you are correct. The link had all the google tracking crap at the end of it. I've edited to remove that. I just saw "google" in the link and got carried away... my bad. – FreeMan Feb 18 '24 at 22:11